I finally got the burner to light and stay burning. Using the motor wire to run the air solenoid won't work. If you use the motor wire to run the air solenoid, it will light and the eye will see flame before the 15 second pre purge, and the system will shut down. You have to use the VALVE TERMINALS to turn on the air solenoid. I don't know what the 15 second pre purge (associated with the valve terminals) is designed to do, but you have to wait 15 seconds before you make a flame, or else the system will shut down. I don't use a air solenoid. I have a on board air compressor (a Thomas 2660 vacuum pump) without a tank that I'll just turn on and off as needed (see picture). I'll go from the valve terminals to a relay to the air compressor. I've got it wired so the ignitor does NOT stay arcing all the time. Thanks Russ, for all your input.