Commercial Waste Oil Heaters / Re: Reznor ra235 ignition issues.
« on: November 16, 2020, 03:20:06 pm »
3016' +/-100'

Box elder, SD 57719, USA

17
Commercial Waste Oil Heaters / Re: Reznor ra235 ignition issues.
« on: November 16, 2020, 02:51:04 pm »
I would say bright body. Fills the whole chamber and hits the target. I have a decent draft when off. IE pulls the regulator open sometimes even set on max.(6.5)

Didn't sputter until I tried opening the airband and then started shuttering and puffing smoke out of inspection door and even the damper.

Did smoke heavily the whole 5 min which is why I tried opening the airbanda bit.

18
Commercial Waste Oil Heaters / Re: Reznor ra235 ignition issues.
« on: November 16, 2020, 11:24:49 am »
Ok fired it up and let it go for around 5 min. Getting smoke the whole time. Did not have very much raw oil in chamber. Cleaned it ran it and tried once to restart. Airband and shutter settings are 0 and 2 respectively as per manual. Still getting puffs back through the inspection port. Tried to open the airband to a 1 and getting big puff back through baro damper and inspection door and shuttering. Shut down after that.
 What the hell am I doing wrong? I've never felt this incompetent. I've rebuilt my duramax engine and it wasn't this frustrating.

19
Commercial Waste Oil Heaters / Re: Reznor ra235 ignition issues.
« on: November 14, 2020, 02:32:36 pm »
I don't doubt that. I have tried playing my case about it. Only reason I put up with it so far with the landlord is cheap rent 6 month lease. Downside is that he's older and not experienced. He purchased at auction and with the work I've done so far he's married to it now. I was going to just buy a NG heater and have them run a line but he's opposed to that so now I'm married to it.

20
Commercial Waste Oil Heaters / Re: Reznor ra235 ignition issues.
« on: November 14, 2020, 01:50:41 pm »
For sure once it's reliable it will stay above 50⁰.

I'm locked into this as primary heat source. (Rented building)
I'm not opposed as my previous shop was 100% reliable for years.

I will let it run for longer on stock air settings to see what it looks like.

Is there a good estimate of what the baro regulator should be? I'm know it changes as it gets up to temp and I should wait for that. I was just worried about the puffs of smoke coming out of the inspection port and a back fire situation.

21
Commercial Waste Oil Heaters / Re: Reznor ra235 ignition issues.
« on: November 14, 2020, 12:46:44 pm »
No carbon built up on the nozzle. Went back together ok.

Drained water off the bottom previously over a couple days. (Maybe 2 gallons) I've had waste oil heaters before so knew enough to do that just never had to trouble shoot it. Was a clean burn and already installed.

Do I need to add a magnetic tank heater to insure above 50⁰? I've never had to do that although once the heater gets going reliably it may not be necessary.... it's a reznor single wall indoor 250gal tank and stand.

Thank you for the help and experience.

22
Commercial Waste Oil Heaters / Re: Reznor ra235 ignition issues.
« on: November 14, 2020, 11:46:44 am »
It's blowing past the nozzle but more straight outand not down. I'd guess total length to be 3/4" long.

Used motor oil of unknown quality presumably fired ok previously. (Heater was purchased at auction and functional before being moved) was going to try a different source. Would a can of diesel be advised? I figured since I could light it with a torch and that it did fire itself the one time the oil was ok.

Oil in the storage tank is probably chilly. I haven't measured that but ambient temp in shop is 45 to 55 degrees temporarily heated to 62-65 degrees with a propane convection heater. (I've got two CO monitors working one via security system)

No way of knowing the tech support knowledge. He told me to clean the nozzle by taking it apart (two pieces) and that was about it. Hard to get a hold of. (Over an hr on hold) local HVAC advised to call them because "that's what we'd do and charge you $65 an hr anyway".

I have a draft but not measured. (It pulls smoke in to unit heater inspection door and at baro regulator) would too little draft have a no light situation. From the manual I can leave my air band and shutter at 0 and 2 respectively? Would this be an issue? I've tried to adjust both from 0 to 5 with no change. I did observe the arc with the head out and with the Airband open it blows it up away from the nozzle like too much air pressure. I have since turned it down other than try to adjust the flame once lit and an I'm out of my element there. Will likely try to find someone experienced to adjust with instruments but figured one problem at a time.


I should add that outside temps are 32-55 degrees and my altitude is 3020'.

23
Commercial Waste Oil Heaters / Reznor ra235 ignition issues.
« on: November 14, 2020, 04:38:39 am »
I have a ra235 that I have installed and I'm having trouble getting it to fire on its own.

 It fired once the very first time I finished the stack install. It wouldn't restart so I pulled the assembly and had a carbon bridge on the electrodes so I plucked it off. After lighting the one time it won't fire.

 So far I've adjusted the electrodes, cleaned the nozzle thoroughly, confirmed that the preheaters are hot and confirmed fog inside the chamber. I have confirmed via mirror that the electrodes gets a good arc and blows when the blower turns on. I've adjusted the gun position. The oil and air compressor pump aren't adjustable. I've talked with reznor support with no help. I can light it with a torch but will not light by itself even after letting it run and trying to restart warm after shutting down. I've changed the air band settings around from 0 to 4 on both and haven't set the draft regulator yet outside of the settings the reznor support suggested at initially 4. When I get it going with the torch it does puff white smoke out of the inspection door. I have not let it run for 5 minutes as I'm worried about doing damage.

 I haven't found much luck hiring an hvac company to come look at it due to COVID-19 and the one I did find with experience told me to call reznor support.